CT1 and CT2

Perhaps a rather rudimentary question but what is “full mode” protection? I assume that it is a combination of common and differential modes but it seems to me that it is generally common mode that is provided.
Parents
  • CCSparkingchip:

    Quote:

     

    An SPD configuration based on connection type 2 (CT2) is required on a TT earth arrangement if the SPD is upstream of the RCD. The RCD being downstream of the SPD would not operate should the SPD become defective.




     




    I am still thinking about that ?


Reply
  • CCSparkingchip:

    Quote:

     

    An SPD configuration based on connection type 2 (CT2) is required on a TT earth arrangement if the SPD is upstream of the RCD. The RCD being downstream of the SPD would not operate should the SPD become defective.




     




    I am still thinking about that ?