wallywombat:Zoomup:It is not always possible to easily fuse down before a bathroom or shower room light. I thought that your previous question was about to trick me. 521.8.2 does not apply, as I am only dealing with ONE final circuit, that of the lighting circuit feeding a single timer extractor fan. No probs. here.
I think the argument here is that by having separate fuses on the L and SL you have effectively created two final circuits but with a single device connected to both circuits. Which creates all sorts of potential problems. For example even with a fuse removed, the load side of the fuse holder may still be live.
The fuse holders are all insulated grid type in a suitable insulated enclosure. There is no shock risk as the terminals are recessed.
Z.
wallywombat:Zoomup:It is not always possible to easily fuse down before a bathroom or shower room light. I thought that your previous question was about to trick me. 521.8.2 does not apply, as I am only dealing with ONE final circuit, that of the lighting circuit feeding a single timer extractor fan. No probs. here.
I think the argument here is that by having separate fuses on the L and SL you have effectively created two final circuits but with a single device connected to both circuits. Which creates all sorts of potential problems. For example even with a fuse removed, the load side of the fuse holder may still be live.
The fuse holders are all insulated grid type in a suitable insulated enclosure. There is no shock risk as the terminals are recessed.
Z.