Also the label reg i was thinking of is 514.11.1 it does say not capable of being isolated by a single device, and you could argue the 6A mcb does this, but then so does the main switch and cut out. I think the intention is that it warns of a possible danger of live parts if one of the fuses blows and the fan dont work.
The notice "shall be fixed in each position where there are live parts which are not capable of being isolated by a single device."
The fan can be isolated by the single lighting M.C.B.
or the 3 pole fan isolator.
Also there are no live parts accessible to cause danger. Everything is enclosed and/or insulated.
So 514.11.1 does not apply.
It might apply to say a night storage heater with a normal on peak heater build in as well as the off peak, where there are two distinct supplies with two different supply switches.
Z.
Also the label reg i was thinking of is 514.11.1 it does say not capable of being isolated by a single device, and you could argue the 6A mcb does this, but then so does the main switch and cut out. I think the intention is that it warns of a possible danger of live parts if one of the fuses blows and the fan dont work.
The notice "shall be fixed in each position where there are live parts which are not capable of being isolated by a single device."
The fan can be isolated by the single lighting M.C.B.
or the 3 pole fan isolator.
Also there are no live parts accessible to cause danger. Everything is enclosed and/or insulated.
So 514.11.1 does not apply.
It might apply to say a night storage heater with a normal on peak heater build in as well as the off peak, where there are two distinct supplies with two different supply switches.
Z.