Installation of a generator for a house.

Hello all,


I'm moving house, (been here for over 42 years'!!), and one of the first items on my mind is installing an electrical generator.


SO; I guess there will be contactors / switch gear etc as I would like it to be 'automatic', (OR, maybe 'manual' too), changing from incoming to the generator.


a; What would be the best type of generator to purchase? Load wise? I'm not too worried as the bigger the load the bigger the           generator would need to be as long as I could run the basics within the house.


b; What switch gear would be appropriate?


I would't fancy the idea of switching tails around on a Henley block each time I needed the generator to be in use!!


Thanks, in advance!


regards... Tom
Parents
  • PG:
    broadgage:

    Is there any need to innvolve the DNO ? I would have thought not as a changeover switch is to be used, with no question of paralell running, backfeeding, or need for synchronising. 

     


    The addition of the changeover switch modifies the DNO connections between the meter and the Consumer Unit. Also the DNO fuses need pulling.

    UKPN advice is to fill in the form for the modification of their network plus a G99 form (even though there is no paralleling planned - it is "A switched alternative supply")

    The DNO have a right to witness that the interlocks preventing paralleling are effective - In practice, they (UKPN) don't exercise it for small installations.



    No pulling of service fuses, nor modification of  DNO connections between meter and consumer unit would be needed if the work was done in the way that I suggest.


    1) Install the new changeover switch. Take the mains input into this switch from a 30/32 amp circuit in the existing consumer unit. Connect the generator input  to the generator.


    2) Install a new 6 or 8 way consumer unit, connected to the output of the changeover switch.


    3) Transfer the existing lighting circuits from the old consumer unit to the new consumer unit.

         Transfer from the old consumer unit to the new consumer unit any dedicated circuits for central heating or other low power high priority loads.

       Install a new 10 amp circuit from new consumer unit to a single red socket in the kitchen.

       Install 2 or 3 new 4 amp circuits to twin red sockets as needed, and as earlier described.



         




     


Reply
  • PG:
    broadgage:

    Is there any need to innvolve the DNO ? I would have thought not as a changeover switch is to be used, with no question of paralell running, backfeeding, or need for synchronising. 

     


    The addition of the changeover switch modifies the DNO connections between the meter and the Consumer Unit. Also the DNO fuses need pulling.

    UKPN advice is to fill in the form for the modification of their network plus a G99 form (even though there is no paralleling planned - it is "A switched alternative supply")

    The DNO have a right to witness that the interlocks preventing paralleling are effective - In practice, they (UKPN) don't exercise it for small installations.



    No pulling of service fuses, nor modification of  DNO connections between meter and consumer unit would be needed if the work was done in the way that I suggest.


    1) Install the new changeover switch. Take the mains input into this switch from a 30/32 amp circuit in the existing consumer unit. Connect the generator input  to the generator.


    2) Install a new 6 or 8 way consumer unit, connected to the output of the changeover switch.


    3) Transfer the existing lighting circuits from the old consumer unit to the new consumer unit.

         Transfer from the old consumer unit to the new consumer unit any dedicated circuits for central heating or other low power high priority loads.

       Install a new 10 amp circuit from new consumer unit to a single red socket in the kitchen.

       Install 2 or 3 new 4 amp circuits to twin red sockets as needed, and as earlier described.



         




     