says it should comply with 543.7.1 and 543.7.1.204 says connections should be made at all points throughout the circuit, so a ring would not be allowed, more like two ladders. There seems to be a contradiction here
543.7.1.204 Where two protective conductors are used in accordance with Regulation 543.7.1.203(iii), the ends of the protective conductors shall be terminated independently of each other at all connection points throughout the circuit, e.g. the distribution board, junction boxes and socket-outlets. This requires an accessory to be provided with two separate earth terminals.
says it should comply with 543.7.1 and 543.7.1.204 says connections should be made at all points throughout the circuit, so a ring would not be allowed, more like two ladders. There seems to be a contradiction here
543.7.1.204 Where two protective conductors are used in accordance with Regulation 543.7.1.203(iii), the ends of the protective conductors shall be terminated independently of each other at all connection points throughout the circuit, e.g. the distribution board, junction boxes and socket-outlets. This requires an accessory to be provided with two separate earth terminals.