AJJewsbury:
...so just taking an extra c.p.c. direct from the last accessory back to the DB is going to be simpler and easier.
..
- Andy.
Hi Andy, i see that solution being allowed in 543.7.2.201 (ii) (a) and possibly (b) but the start of 543.7.2.201 says it should comply with 543.7.1 and 543.7.1.204 says connections should be made at all points throughout the circuit, so a ring would not be allowed, more like two ladders. There seems to be a contradiction here.
edit; 1 ladder not 2 :)
says it should comply with 543.7.1 and 543.7.1.204 says connections should be made at all points throughout the circuit, so a ring would not be allowed, more like two ladders. There seems to be a contradiction here
543.7.1.204 Where two protective conductors are used in accordance with Regulation 543.7.1.203(iii), the ends of the protective conductors shall be terminated independently of each other at all connection points throughout the circuit, e.g. the distribution board, junction boxes and socket-outlets. This requires an accessory to be provided with two separate earth terminals.
wessex:
I can see having two cpc's per earth terminal could produce a weakness/reliability issue.
Agreed, if it were required by BS7671 to have a continuous earthing (and possibly live) conductor in radial circuits it would mitigate a failed termination causing loss of earthing in another accessory. The conductor is bent and looped into the terminal, thus maintaining continuity. It is a trickier wiring job, looping cables into accessory boxes without cutting the cable, leaving enough slack, but not too much. Note that this would not be allowed by 543.7.1.204 if there was a ring, since each end needs to be terminated in separate terminals, but would be allowed by it if there was a parallel "ladder" arrangement with two CPCs