UKPN service head to smart meter - Advice and options?

Former Community Member
Former Community Member
Situation - first floor maisonette

UKPN Service head (60A fuse) TN-S is located in ground floor flat with no access for first floor.  Riser cables (VIR badly degraded) run inside brickwork up to another cutout fuse (60A).  Modern cables then loop into smart meter.  UKPN say they are not responsible for the riser - EDS 08-1103 section 6.1 - even though EPN as it was then installed it (although the cutout is theirs and technically only they are allowed to remove the fuse - my thoughts?).  UKPN won't pay for the work so that sits with the client unless anyone can tell me differently?

So, what's the best way to achieve this?  Need to upgrade the cable to 25mm2 (and probably ask to upgrade fuse to 100A) and it's not practical to start digging out the walls, not least because prolonged access to downstairs is not really an option.  Therefore external?  Best method/option?

Thanks in advance


Images - degraded VIR cable; upstairs cutout; downstairs service head
441e1955118398d5c372d5c581f9b1f4-huge-2021-03-08-11.11.21.jpg4d4b6764c4e77cfb446cace0ef9fb2cd-huge-2021-03-08-11.10.56.jpg
b96c361424b4d58634fc968632e95a41-huge-2021-03-08-17.06.50.jpg
Parents
  • This situation is obviously a very serious one making a shock and/or fire risk very possible. As you know it needs serious urgent attention. I would try to escalate the claim for renewals to be undertaken without delay.  Perhaps a report of a burning sell and concerns about fire would help? If you undertake the work, a switch fuse will be needed at the meter position and a new sub-main installed to the upper level. I would also assume TN-C-S despite what you can see.


    Edit add. I would be tempted to get repairs undertaken immediately whatever the cost to the client. It is vital to ensure safety. Safety first, cost second. 


    Can you run a new sub-main externally?


    Z.
Reply
  • This situation is obviously a very serious one making a shock and/or fire risk very possible. As you know it needs serious urgent attention. I would try to escalate the claim for renewals to be undertaken without delay.  Perhaps a report of a burning sell and concerns about fire would help? If you undertake the work, a switch fuse will be needed at the meter position and a new sub-main installed to the upper level. I would also assume TN-C-S despite what you can see.


    Edit add. I would be tempted to get repairs undertaken immediately whatever the cost to the client. It is vital to ensure safety. Safety first, cost second. 


    Can you run a new sub-main externally?


    Z.