This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

UKPN service head to smart meter - Advice and options?

Former Community Member
Former Community Member
Situation - first floor maisonette

UKPN Service head (60A fuse) TN-S is located in ground floor flat with no access for first floor.  Riser cables (VIR badly degraded) run inside brickwork up to another cutout fuse (60A).  Modern cables then loop into smart meter.  UKPN say they are not responsible for the riser - EDS 08-1103 section 6.1 - even though EPN as it was then installed it (although the cutout is theirs and technically only they are allowed to remove the fuse - my thoughts?).  UKPN won't pay for the work so that sits with the client unless anyone can tell me differently?

So, what's the best way to achieve this?  Need to upgrade the cable to 25mm2 (and probably ask to upgrade fuse to 100A) and it's not practical to start digging out the walls, not least because prolonged access to downstairs is not really an option.  Therefore external?  Best method/option?

Thanks in advance


Images - degraded VIR cable; upstairs cutout; downstairs service head
441e1955118398d5c372d5c581f9b1f4-huge-2021-03-08-11.11.21.jpg4d4b6764c4e77cfb446cace0ef9fb2cd-huge-2021-03-08-11.10.56.jpg
b96c361424b4d58634fc968632e95a41-huge-2021-03-08-17.06.50.jpg
Parents
  • I agree with Andy, those tails in the picture are not in immediate danger of failure as far as I can see. This is not a case of panic. The old tails we are told travel up to another meter, in the flat above, and the meter operator will be responsible for the tails between the cutout and the meter (as no one else can connect them) and there is potentially a risk of abstraction. I suggest you contact them and point out that their installation is unsatisfactory. These cables do not belong to the consumer and are not part of a BNO installation. If you really need more power then the DNO will supply another distribution cable at a considerable cost, to supply the upstairs flat alone.
Reply
  • I agree with Andy, those tails in the picture are not in immediate danger of failure as far as I can see. This is not a case of panic. The old tails we are told travel up to another meter, in the flat above, and the meter operator will be responsible for the tails between the cutout and the meter (as no one else can connect them) and there is potentially a risk of abstraction. I suggest you contact them and point out that their installation is unsatisfactory. These cables do not belong to the consumer and are not part of a BNO installation. If you really need more power then the DNO will supply another distribution cable at a considerable cost, to supply the upstairs flat alone.
Children
No Data