davezawadi (David Stone):
I agree with Andy, those tails in the picture are not in immediate danger of failure as far as I can see. This is not a case of panic. The old tails we are told travel up to another meter, in the flat above, and the meter operator will be responsible for the tails between the cutout and the meter (as no one else can connect them) and there is potentially a risk of abstraction. I suggest you contact them and point out that their installation is unsatisfactory. These cables do not belong to the consumer and are not part of a BNO installation. If you really need more power then the DNO will supply another distribution cable at a considerable cost, to supply the upstairs flat alone.
Hi David
UKPN did come out before I posted this and the engineer said that they were not responsible for the riser; their responsibility ended at the service head which is in the downstairs flat. I did phone customer services to question that and did get it escalated. That's when they quoted EDS 08-1103 section 6.1. Definitely pre 1972 so not between 1972 -2013. So not quite sure what can be done apart from the client paying for it. It definitely needs sorting asap! Anybody on here have a successful 'dialogue' with a DNO in a similar situation and get a successful resolution. The engineer hinted that they may just come, cut off the supply until it's sorted and tough luck on the client ...
davezawadi (David Stone):
I agree with Andy, those tails in the picture are not in immediate danger of failure as far as I can see. This is not a case of panic. The old tails we are told travel up to another meter, in the flat above, and the meter operator will be responsible for the tails between the cutout and the meter (as no one else can connect them) and there is potentially a risk of abstraction. I suggest you contact them and point out that their installation is unsatisfactory. These cables do not belong to the consumer and are not part of a BNO installation. If you really need more power then the DNO will supply another distribution cable at a considerable cost, to supply the upstairs flat alone.
Hi David
UKPN did come out before I posted this and the engineer said that they were not responsible for the riser; their responsibility ended at the service head which is in the downstairs flat. I did phone customer services to question that and did get it escalated. That's when they quoted EDS 08-1103 section 6.1. Definitely pre 1972 so not between 1972 -2013. So not quite sure what can be done apart from the client paying for it. It definitely needs sorting asap! Anybody on here have a successful 'dialogue' with a DNO in a similar situation and get a successful resolution. The engineer hinted that they may just come, cut off the supply until it's sorted and tough luck on the client ...
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site