I'm not sure of the wording in GN 5, but electrodes to keep the voltage down in the case of a broken PEN is a well known technique - very frequently used with low power installations, such as individual street lighting columns. For larger installations (say a 100A domestic) the required resistance would be so low as to be practically impossible to achieve.
I'm not sure of the wording in GN 5, but electrodes to keep the voltage down in the case of a broken PEN is a well known technique - very frequently used with low power installations, such as individual street lighting columns. For larger installations (say a 100A domestic) the required resistance would be so low as to be practically impossible to achieve.