63amp connectors
Former Community Member
Hi I need to join two cables I’d like to do it under the floor so maintenance free would’ve best but I could do it in a conduit terminal box on the outside wall. What connectors would people recommend
If it will get wet, the same sort of crimps could be used in a resin filled joint, the 'clamshells' will fit the SWA well, but will need a grommet or similar at the T and E end of things to keep the resin in while it sets.
If you had wanted a screw joint I'd be looking at line taps.
If it will get wet, the same sort of crimps could be used in a resin filled joint, the 'clamshells' will fit the SWA well, but will need a grommet or similar at the T and E end of things to keep the resin in while it sets.
If you had wanted a screw joint I'd be looking at line taps.