ff4dd4e3be3fd92a2860545df50ddca9-huge-5418b436-fc4e-47b3-a594-4fea60cb12cd.jpgI see this a lot on sites where they’ve got an armoured cable with an earthing ring/banjo connecting the armour to an extraneous conductive part. Should there also be main bonding run as well? Common thing I see is cable tray being supplementary bonded of a local isolator usually 6mm or 10mm?
Parents
  • MrJack96:
    ff4dd4e3be3fd92a2860545df50ddca9-huge-5418b436-fc4e-47b3-a594-4fea60cb12cd.jpgI see this a lot on sites where they’ve got an armoured cable with an earthing ring/banjo connecting the armour to an extraneous conductive part. Should there also be main bonding run as well? Common thing I see is cable tray being supplementary bonded of a local isolator usually 6mm or 10mm? 


    Interesting. The top of the picture is cut off, but I guess it's only got the switch and plastic box on it, nothing else?


    I would have said in this case, it's possibly neither an extraneous-conductive-part, nor an exposed-conductive-part.


    It certainly depends on what you term "installation" (definition in Part 2 of BS 7671 is very open to interpretation), and also whether PME conditions (and G12/4) applies, as to whether there needs to be a "main bonding run" from the entire installation MET or not.


Reply
  • MrJack96:
    ff4dd4e3be3fd92a2860545df50ddca9-huge-5418b436-fc4e-47b3-a594-4fea60cb12cd.jpgI see this a lot on sites where they’ve got an armoured cable with an earthing ring/banjo connecting the armour to an extraneous conductive part. Should there also be main bonding run as well? Common thing I see is cable tray being supplementary bonded of a local isolator usually 6mm or 10mm? 


    Interesting. The top of the picture is cut off, but I guess it's only got the switch and plastic box on it, nothing else?


    I would have said in this case, it's possibly neither an extraneous-conductive-part, nor an exposed-conductive-part.


    It certainly depends on what you term "installation" (definition in Part 2 of BS 7671 is very open to interpretation), and also whether PME conditions (and G12/4) applies, as to whether there needs to be a "main bonding run" from the entire installation MET or not.