M. Joshi:
What are the requirements for determining whether surge protection should be installed in industrial enclosures? The enclosures will typically have motor drives, emergency stop systems and sensors/data acquisition.
Are Type 2 & 3 surge protection modules commonplace?
Chapter 44 of B.S. 7671. Protection Against Voltage Disturbances.
443.4 Over Voltage Control.
Protection against over Voltages shall be provided where the consequences caused by the over Voltage could:
(i) result in serious injury to, or loss of human life, OR
(ii) result in interruption of public services and/or damage to cultural heritage, OR
(iii) result in interruption of commercial or industrial activity, OR
(iv) affect large number of co-ordinated individuals.
For all other cases a risk assessment according to Reg. 443.5 shall be performed........
New surge protective devices (SPDs) - for all types of installation and all risk levels - YouTube
Z.
What are the requirements for determining whether surge protection should be installed in industrial enclosures? The enclosures will typically have motor drives, emergency stop systems and sensors/data acquisition.
wallywombat:
There's also the 10m guideline. Due to some sort of resonance effect that I don't profess to understand, a spike reduced to 1.5kV at a DB/SPD can double back up to 3kV at a point further than 10m downstream from the SPD. Which is one reason for having a type 2 SPD at each DB supplied by a submain from the main DB.
WW, have you got a reference for that please? (I wouldn't even try to understand it all.)
Chris Pearson:WW, have you got a reference for that please? (I wouldn't even try to understand it all.)
The BEAMA GUIDE TO SURGE PROTECTION DEVICES (SPDs) document, section 6.2.2
wallywombat:
There's also the 10m guideline. Due to some sort of resonance effect that I don't profess to understand, a spike reduced to 1.5kV at a DB/SPD can double back up to 3kV at a point further than 10m downstream from the SPD. Which is one reason for having a type 2 SPD at each DB supplied by a submain from the main DB.
It's yer actual oscillation wot does it. The bit I did glean was this: In addition to keeping connecting leads short, they should be tightly bound together over as much of their length as possible, using cable ties or spiral wrap. This is very effective in cancelling inductance and hence inductive voltage dropped onto the connecting leads.
Z.
Zoomup:Chapter 44 of B.S. 7671. Protection Against Voltage Disturbances.
Probably doesn't apply to these industrial premises.
In addition, the cable bursting strengths for multicore and cleated single cores requires to be within the design. I remember in a Scottish steelworks on 24 hour shifts when sleeping in a howff - (in an unused distribution transformer bay). During the early hours of a Sunday morning when there was no production; an armoured cable to the crutch of an 11kV distribution transformer blew out, it was completely vapourised with copper splatter on the brick wall. The 5 of us sleeping on nightshift made a beeline for the door and in the darkness. I never loitered around live transformers after that. Voltage regulation in the silent hours was probably the cause.