wallywombat:
There's also the 10m guideline. Due to some sort of resonance effect that I don't profess to understand, a spike reduced to 1.5kV at a DB/SPD can double back up to 3kV at a point further than 10m downstream from the SPD. Which is one reason for having a type 2 SPD at each DB supplied by a submain from the main DB.
It's yer actual oscillation wot does it. The bit I did glean was this: In addition to keeping connecting leads short, they should be tightly bound together over as much of their length as possible, using cable ties or spiral wrap. This is very effective in cancelling inductance and hence inductive voltage dropped onto the connecting leads.
Z.
wallywombat:
There's also the 10m guideline. Due to some sort of resonance effect that I don't profess to understand, a spike reduced to 1.5kV at a DB/SPD can double back up to 3kV at a point further than 10m downstream from the SPD. Which is one reason for having a type 2 SPD at each DB supplied by a submain from the main DB.
It's yer actual oscillation wot does it. The bit I did glean was this: In addition to keeping connecting leads short, they should be tightly bound together over as much of their length as possible, using cable ties or spiral wrap. This is very effective in cancelling inductance and hence inductive voltage dropped onto the connecting leads.
Z.