Oven & hob on 13amp fused spur

Former Community Member
Former Community Member
I’ve come across an electric oven and gas hob on a cooker circuit, the cooker switch feeds a 13a fused spur which powers both the Oven & hob, hard wired into a 32amp junction box.
the oven is rated at 13 amps but the hob 3 amps Is this acceptable as the hob is protected by a 13 amp fuse?

Parents
  • It will be fine, the uncertainty in the rating if the 13A fuse will be more than the average load of the gas - 4 sparks 3 times a day and perhaps a clock.

    The cable to the hob ought to be large enough to not fail during the blowing if the 13A fuse, and that is the only issue that may be a problem.

    M.
Reply
  • It will be fine, the uncertainty in the rating if the 13A fuse will be more than the average load of the gas - 4 sparks 3 times a day and perhaps a clock.

    The cable to the hob ought to be large enough to not fail during the blowing if the 13A fuse, and that is the only issue that may be a problem.

    M.