mapj1:
It will be fine, the uncertainty in the rating if the 13A fuse will be more than the average load of the gas - 4 sparks 3 times a day and perhaps a clock.
The cable to the hob ought to be large enough to not fail during the blowing if the 13A fuse, and that is the only issue that may be a problem.
M.
Yes, that was my issue. the cable supplying the hob is 0.75mm2 but protected by a 13a fuse
both the oven & hob are protected by the same fuse (fused spur)
Sorry, the 3 amp is what the hob manufacturer recommends for similar hobs (hob uses 6w for ignition)
it does seem a strange way to install but I would guess the oven / hob has been replaced over the years
mapj1:
It will be fine, the uncertainty in the rating if the 13A fuse will be more than the average load of the gas - 4 sparks 3 times a day and perhaps a clock.
The cable to the hob ought to be large enough to not fail during the blowing if the 13A fuse, and that is the only issue that may be a problem.
M.
Yes, that was my issue. the cable supplying the hob is 0.75mm2 but protected by a 13a fuse
both the oven & hob are protected by the same fuse (fused spur)
Sorry, the 3 amp is what the hob manufacturer recommends for similar hobs (hob uses 6w for ignition)
it does seem a strange way to install but I would guess the oven / hob has been replaced over the years