Oven & hob on 13amp fused spur

Former Community Member
Former Community Member
I’ve come across an electric oven and gas hob on a cooker circuit, the cooker switch feeds a 13a fused spur which powers both the Oven & hob, hard wired into a 32amp junction box.
the oven is rated at 13 amps but the hob 3 amps Is this acceptable as the hob is protected by a 13 amp fuse?

Parents
  • A short length of 0,75mm will be fine protected by a 13A fuse, or indeed a 16A breaker, so long as the load at the end of it is not sensibly going to be more than a few amps, and the credible failure mechanisms are either dead short or total open circuit.

    If it was feeding a socket,  that could not be guaranteed, as someone may plug in more than the  hob. However, hard wired like this I think the most likely faults are it stops working one day, or the cable gets pinched or melted by the oven, and the fault is a dead short. Both of those are safe outcomes.

    As others have noted a lot of short duration 13A appliances, such as kettles, toasters etc have a surprisingly thin lead anyway, and come to no harm - 0.75mm can carry 13A for some time, and against a dead short, the 13A fuse blows before the wire gets too hot. We could try the Adiabatic Formula on this if we felt the urge. I don't intend to as I've had an odd  beer this evening, and  that is when I post maths with errors, which is bad.

    Mike
Reply
  • A short length of 0,75mm will be fine protected by a 13A fuse, or indeed a 16A breaker, so long as the load at the end of it is not sensibly going to be more than a few amps, and the credible failure mechanisms are either dead short or total open circuit.

    If it was feeding a socket,  that could not be guaranteed, as someone may plug in more than the  hob. However, hard wired like this I think the most likely faults are it stops working one day, or the cable gets pinched or melted by the oven, and the fault is a dead short. Both of those are safe outcomes.

    As others have noted a lot of short duration 13A appliances, such as kettles, toasters etc have a surprisingly thin lead anyway, and come to no harm - 0.75mm can carry 13A for some time, and against a dead short, the 13A fuse blows before the wire gets too hot. We could try the Adiabatic Formula on this if we felt the urge. I don't intend to as I've had an odd  beer this evening, and  that is when I post maths with errors, which is bad.

    Mike