ebee:
A 3 Amp hob won`t cook much will it Tom?
Hello Ebee!!
The hob is gas and it uses the required electrics for 'ignition' only. So, nothing much in wattage?
I was thinking, (not a good point, for me, I know, haha), maybe remove the JB and fix a 'dual' pattress so one side can be fitted with a Sw't spur and the other with a plug top OR, 2 x switch spurs???
regards... Tom
Tomgunn:
What is the size of the cable, feeding the JB?
0.75mm2 is rated at 6 amps... I know this isn't feeding the JB!
6mm (or possibly 4mm) feeding to the Fused spur, then 2.5mm to the JB the circuit is protected by a 20a MCB
To complicate matters the cooker circuit has been turned into a radial circuit as there is also a socket outlet which is used for a fridge
The socket outlet is on 2.5mm I guess this is why the circuit has a 20a MCB
So its CU 20a MCB >>> Cooker Switch with socket (switched side feeding 13a fused spur for oven / hob ) >>> Socket outlet
Denis McMahon:
I agree with others in that there is not a safety issue. However it is a rather untidy arrangement, and not within the spirit of the Wiring Regulations, let alone the letter.
I am not keen on hard wiring appliances to the permanent mains wiring. If two spur points were provided, then it would be easy to remove either the oven or the hob for servicing. Even consider two 13 A sockets that the appliances would plug into. Quicker and easier still to remove for servicing.
I totally agree with the idea of 13a sockets, but the oven manual states that it must be hard wired to a Circuit with 13a protection, And wired with a minimum 4.0mm three core cable or T&E
The oven is rated at 2200W, why would they consider 4.0mm as the minimum, surely 1.5mm would be acceptable?