AJJewsbury:
Sounds messy, and check with the hob manufacturer's instructions.
I doubt there is a real safety issue however - just about all consumer appliances these days will be designed the same for sale right across Europe - and 3A fuses are unknown outside of the UK/Ireland (and a couple of small ex-Empire areas) - so practically everything that could be plugged into a socket is expected to function safely on a 16A or even 20A OPD.
- Andy.
Hello Andy...
I have had to read this several times... I don't think he means there's a '3 amp' fuse ~ rather that the hob is rated at '3 amps.'
regards...
I don't think he means there's a '3 amp' fuse ~ rather that the hob is rated at '3 amps.'
mapj1:
It will be fine, the uncertainty in the rating if the 13A fuse will be more than the average load of the gas - 4 sparks 3 times a day and perhaps a clock.
The cable to the hob ought to be large enough to not fail during the blowing if the 13A fuse, and that is the only issue that may be a problem.
M.
Yes, that was my issue. the cable supplying the hob is 0.75mm2 but protected by a 13a fuse
both the oven & hob are protected by the same fuse (fused spur)
Sorry, the 3 amp is what the hob manufacturer recommends for similar hobs (hob uses 6w for ignition)
it does seem a strange way to install but I would guess the oven / hob has been replaced over the years