Double pole RCD

Is there anything preventing us from using these type of RCDs for a 55-0-55 circuit?


the picture shows the original set up. And the replacement b27da3454a5814fd623eb7a7fef4edcb-huge-87007dcb-a17d-44db-b7f4-06ceebdf5a1f.jpg

c68f8770359e16551ccee99a957913b2-huge-1935ff0d-6fd0-4eed-9ae1-8224f6776c3a.png
Parents
  • It's quite simple - if an RCD is suitable for use on 110 V systems, the manufacturer will declare that voltage range ... if not, it won't be declared, as the RCD functionality to BS EN 61008 or BS EN 61009 is not assured.


    It's not simply a case of whether the test button will or won't work.


    To fit a device in an electrical system other than one it is rated for, in a workplace, could lead to a breach of Regulation 5 of the Electricity at Work Regulations. Art. 85 of the Memorandum of Guidance on EAWR says:
    85 Electrical equipment should be used within the manufacturer’s rating (continuous, intermittent or fault rating as appropriate) and in accordance with any instructions supplied with the equipment.

     


    So, check the manufacturer says it's OK for 110 V AC systems ...

Reply
  • It's quite simple - if an RCD is suitable for use on 110 V systems, the manufacturer will declare that voltage range ... if not, it won't be declared, as the RCD functionality to BS EN 61008 or BS EN 61009 is not assured.


    It's not simply a case of whether the test button will or won't work.


    To fit a device in an electrical system other than one it is rated for, in a workplace, could lead to a breach of Regulation 5 of the Electricity at Work Regulations. Art. 85 of the Memorandum of Guidance on EAWR says:
    85 Electrical equipment should be used within the manufacturer’s rating (continuous, intermittent or fault rating as appropriate) and in accordance with any instructions supplied with the equipment.

     


    So, check the manufacturer says it's OK for 110 V AC systems ...