HV RMU safe working distances

Hi there can anyone point me to and specific regulations that highlight the requirements for working on 11kV?


I’m specifically looking at an 11kV switch disconnector on a TX but would be good to know if this is the same for an RMU.  


  • Former Community Member
    0 Former Community Member
    Would your  High Voltage Senior Authorised Person be able to advise as they are the ones that will be operating it?


    Regards


    BOD
  • No they won't commit to a distance and I didn't know if there is a standard for this.
  • I agree with BOD that it sounds like you need to talk to the SAP. After all, presumably they'll be issuing you the Permit to Work (or LOA etc), so they'll need to see your RAMS anyway, and you know the setup.


    What precisely are you doing, and what do you want a safe working distance from?
  • As others have said, you need to talk with one of your company’s HV Senior Authorised Persons. From your comments, I don’t believe that you hold an HV Competent Persons authorisation, so I am unable to comment further. 


    Regards,


    Alan.
  • AFAIK, there is no clearly defined distance. It would depend on the nature of the equipment and on what work is to be done.

    There is no simple "tick box" that a certain distance is required and that some lesser distance is prohibited.


    Most such equipment is operated by DNOs, and they presumably have codes of practice regarding working space, this could be a useful starting point for similar equipment in private hands.
  • The closest standard ive got its IEEE 1584 which states a clear working distance of aprox 1m
  • Former Community Member
    0 Former Community Member

    The closest standard ive got its IEEE 1584 which states a clear working distance of aprox 1m


    Would that be from the end of the wind up/down operating handle or from where the "truck" is pulled clear?


    Regards


    BOD
  • From an 11kV RMU  handle pal ?
  • IEEE 1584 is a standard for working out arc flash and incident energy. This allows you to calculate the rating of protective clothing you need such that the blast from a short circuit is reasonably survivable. At 1m distance, you will be within the arc produced by a short circuit. 

    “An arc flash has the blast energy of several sticks of dynamite, and a temperature hotter than the surface of the sun”. 


    Regards,


    Alan.
  • Former Community Member
    0 Former Community Member
    From an 11kV RMU  handle pal


    So RMU don't have pull out trucks then?


    Regards


    BOD