davezawadi (David Stone):
Well that is interesting Graham because there is no BS number (or even an EN one) on my box of Ideal connectors. Perhaps I am an early adopter and they hadn't printed it on yet. It seems that no one trusts screw terminals any more, which is curious.
Not really curious, the products are too small for sufficient information to be printed on them. However, I can confirm Ideal state compliance with EN 60998 series also ... https://www.idealindustriesemea.com/content/dam/europe/resources/catalogues/IDEAL%20Wire%20Connectors%20DL%20Flyer.pdf
I think even the Ideal screwits are also stated to be compliant and suitable for BS 7671 use!
perspicacious:
So, with this in mind, would a 20 A JB attract any coding on an EICR if found on a 32 A RFC?
OK, I have rummaged around and found an old BS 6220 JB. 2¼" diameter. It is marked, "NOMINAL CABLE 2.5 MM²" and "250 V 20A".
BS 6220 says:
5 Classification
A junction box shall be classified according to:
a) the number of terminals as declared by the manufacturer;
b) the nominal conductor capacity of the terminals, as declared by the manufacturer, which shall be one of the capacities shown in column 1 of Table 2;
c) the method of mounting (e.g. surface or flush).
6 Marking
6.1 All junction boxes shall be durably and legibly
marked with the following:
a) the number of this British Standard, i.e. BS 62201);
b) the name or trade mark of the manufacturer or responsible vendor;
c) the nominal conductor capacity of the terminals, i.e. “n mm2” or “n” ‘ where n is the conductor size in mm2;
d) the rated voltage, e.g. “250 V”. Compliance shall be checked by inspection.
So what we have is a (4-terminal) 2.5 mm² surface mounted JB. There is no current rating!
The BS goes on to specify that at least 2 x the nominal conductor must be accommodated (else it wouldn't be a JB! ? ) and that the test current for the 2.5 mm² version is 30 A.
So the answer, BAD, is "no".
Chris Pearson:perspicacious:
So, with this in mind, would a 20 A JB attract any coding on an EICR if found on a 32 A RFC?OK, I have rummaged around and found an old BS 6220 JB. 2¼" diameter. It is marked, "NOMINAL CABLE 2.5 MM²" and "250 V 20A".
BS 6220 says:
5 Classification
A junction box shall be classified according to:
a) the number of terminals as declared by the manufacturer;
b) the nominal conductor capacity of the terminals, as declared by the manufacturer, which shall be one of the capacities shown in column 1 of Table 2;
c) the method of mounting (e.g. surface or flush).
6 Marking
6.1 All junction boxes shall be durably and legibly
marked with the following:
a) the number of this British Standard, i.e. BS 62201);
b) the name or trade mark of the manufacturer or responsible vendor;
c) the nominal conductor capacity of the terminals, i.e. “n mm2” or “n” ‘ where n is the conductor size in mm2;
d) the rated voltage, e.g. “250 V”. Compliance shall be checked by inspection.
So what we have is a (4-terminal) 2.5 mm² surface mounted JB. There is no current rating!
The BS goes on to specify that at least 2 x the nominal conductor must be accommodated (else it wouldn't be a JB! ? ) and that the test current for the 2.5 mm² version is 30 A.
So the answer, BAD, is "no".
Why? The test current is greater than that for a BS 1363-2 socket-outlet? The voltage and current rating is that of conductors in a cable in a RFC?
What makes it unsuitable for an RFC?
If a single terminal is so good at clamping and maintaining continuity, why the requirement for a secondary earth terminal for some circuit accessories required?
AJJewsbury:I think we have been told that additional sockets MUST have a 13a switch fused spur
I hope that either someone has mis-remembered or the advise has been taken out of context...
- Andy.
The correct answer (which is that an additional socket-outlet (single or double) spurred of an accessory on a ring, provided it is the only additional socket connected to that accessory, does not require a fuse ... provided you don't expect someone to use more than 13 A from that socket-outlet.
It's all there for everyone to see in Appendix 15 to BS 7671. (page 505). It also shows you where you need to use an FCU for the spur.
I guess the mix-up is that FCUs are called "fused spurs", and SFCUs are called "switched fused spurs" by many in the industry.