geoffsd:
The trouble is it is not ALL there in Appendix 15 which is only informative and does not show everything that is possible.
Everything I said is there ... to put every possible permutation of a ring final circuit in any diagram, or even a set of requirements, is of course not possible.
gkenyon:
BS 5733 if memory serves for the 20 A DP switch.
The Low Voltage Directive 2006/95/EC
BS EN 60669-1:1999 + A1:2002 + A2:2008
Modified ISO 22196
Therein lies the “problem” with 20 amp double pole switches being used in kitchens to switch sockets and appliances, that and the fact that a lot of the “installation managers” working for the big shed kitchen companies like MFI attended 16th Edition Wiring Regulations courses and were awarded the C&G, so they could “inspect” the electrical work completed by kitchen fitters.
These “electrical inspectors” would point out the requirements of 537 Isolation and switching and in particular Table 537.4 which states that the 20 amp switches don’t provide isolation, unlike 13 amp SFCU.
That has set the standard for kitchen fitters and kitchen installations for the last twenty years with an insistence that SFCU should be used above work surfaces to control appliances and inaccessible sockets, because you can take the fuse out of them.
Generally that’s fine, until someone uses a SFCU to control a double socket.
Andy B.
Sparkingchip:gkenyon:
BS 5733 if memory serves for the 20 A DP switch.
The Low Voltage Directive 2006/95/EC
BS EN 60669-1:1999 + A1:2002 + A2:2008
Modified ISO 22196
Therein lies the “problem” with 20 amp double pole switches being used in kitchens to switch sockets and appliances, that snow the fact that a lot of the “installation managers” working for the big shed kitchen companies like MFI attended 16th Edition Wiring Regulations courses and were awarded the C&G, so they could “inspect” the electrical work completed by kitchen fitters.
These “electrical inspectors” would point out the requirements of 537 Isolation and switching and in particular Table 537.4 which states that the 20 amp switches don’t provide isolation, unlike 13 amp SFCU.
That has set the standard for kitchen fitters and kitchen installations for the last twenty years with an insistence that SFCU should be used above work surfaces to control appliances and inaccessible sockets, because you can take the fuse out of them.
Generally that’s fine, until someone uses a SFCU to control a double socket.
Andy B.
The switch is OK to remove power and provide control. The appliance plug and socket-outlet can provide isolation for maintenance.
If BS EN 60669-1 is good enough for a cooker switch, which requires a "proper" means of isolation such as the circuit protective device, then it's good enough for an under-counter appliance connected via plug and socket-outlet.
Or the world has gone mad.
The user will not remove the fuse and lock off the appliance overnight, so the switch on the FCU does nothing different. The purpose of providing the above counter switch - removing power for fire safety reasons and emergency switching - is still achieved by providing a switch to BS EN 60669-1 instead of an SFCU ...
Sparkingchip:
Just to complicate it more they would also point out that table says plug and sockets don’t provide emergency switching, so even if the socket was accessible you still needed the SFCU, as the SFCU fulfils all three requirements of isolation, emergency switching and functional switching.
Interesting that a switched socket-outlet can't be used for emergency switching
Regardless of BS 7671 and BS 1363-2 say, people do use them like that ... so the requirements in BS 7671 don't match the real world. An ordinary person wouldn't have any awareness of the difference, and simply switch off at the socket-outlet (if switched) and unplug a portable appliance if they saw smoke coming out of it.
Anyway, no-one said that a single device has to be provided to meet all of the requirements.