Overloaded fused spur, opinion please

I was an industrial electrician and have now come across a domestic wiring issue where nothing appeared wrong with the installation.  Those with more experience will have probably have come across this many times.


The kitchen is supplied by a 2.5mm T&E ring fed from a B32 circuit breaker.  On this ring there is a 13A fused switched spur above the worktop feeding a double socket underneath via 2.5 T&E.  There is a washing machine and a dishwasher plugged into this double socket.  Every so often, I assume when both appliances are heating at the same time, the 13A fuse in the spur blows.  The cable supplying this double socket is in the wall so the current-carrying capacity appears to be 18.5A so this was probably being overloaded as well.


I understand that in the regs diversity covers some aspects of this situation, but this specific situation must occur often surely?  The switched spur gives the ability to switch off the appliance easily without having to pull it out in order to reach the switch, so is surely desirable?


In this case I have installed a second switched fused spur feeding a single socket and converted the other to a single.


Is this a common problem in kitchens?
  • ebee:

    I did not like the look of his one strand of 1.0mm2 conductor in an ashley JB20A  on his security lighting (tungsten halogen) and that`s why I mentioned doubling to him and got his ruf comment.

    I am not aware of anyone else agreeing with him


    The argument against doubling, or twisting two or more conductors together (using pliers) is that the end of the cable(s) may be damaged.


    BS 6220 specifies: Terminals shall be capable of accommodating and clamping at least two conductors two sizes smaller than the designated size, the conductors being solid or stranded. On the basis of a nominal 2.5 mm² conductor size, it follows that your chum's JB has been used appropriately.


  • The client wants sleek, clean lines with glass splash backs or the like, whilst the electrician is peppering the walls with SFCUs.


    I'll own up, in my kitchen I have two 20-amp switches each supplying a single socket for the washing machine and dishwasher, they are tucked away behind the end of the microwave and when I turned them off whilst we went on holiday on our return my wife thought the washing machine had packed up, not even realising that the appliances are switched above the countertop.