Zoomup:
I just came across this for a model CB24. The one that I was told about is a CB25, but may be similar.
https://www.bing.com/videos/search?q=youtube+Alpha+HECB25boiler+repair&docid=607993886868140910&mid=D52708F9D37D3B744551D52708F9D37D3B744551&view=detail&FORM=VIRE
The "he" bit in the name means high efficiency, it is a condensing boiler and newer than that one in the vid, so not the same. Did you find the he cb 25 instructions? You can get a fair way through fault finding as an electrician before doing gas "work".
Not sure whether ebee's air pressure switch fault would be picked up in a flow chart, it is very unusual to have continuity through all 3 terminals
davidwalker2:
Just a thought. I had a similar fault on my WB, the heating was apparently working but the water in the taps was lukewarm and then cold. There did not seem to be anything wrong, except when the the hot water was turned on the boiler would fire up and then go out.
Then I noticed the little pressure gauge that indicates the water pressure in the primary circuit was zero. Re-pressurised and all well.
David
Hello David, the pressure is o.k. at just over 1 bar I seem to recall. Anyway it is in the green range of the pressure gauge, but thanks anyway.
OlympusMons:Zoomup:
Z.The "he" bit in the name means high efficiency, it is a condensing boiler and newer than that one in the vid, so not the same. Did you find the he cb 25 instructions? You can get a fair way through fault finding as an electrician before doing gas "work".
Hello Olympus,
I have been so busy that I have not had a chance to get the fault finding flow chart yet. I did though order a new diverter valve diaphragm repair kit. It is suitable for the Alpha HE 25 and CB33 according to the supplier. It looks the same as the one in the video, and it comes with many new washers and some silicon grease. I may check the micro switch if it is accessible, before any dismantling.
Thanks,
Zoomup:OlympusMons:Zoomup:
Not sure whether ebee's air pressure switch fault would be picked up in a flow chart, it is very unusual to have continuity through all 3 terminalsHello Olympus,
Zoomy, admit it, you just like fixing things. ?
Chris Pearson:Zoomup:OlympusMons:Zoomup:
I have been so busy that I have not had a chance to get the fault finding flow chart yet. I did though order a new diverter valve diaphragm repair kit. It is suitable for the Alpha HE 25 and CB33 according to the supplier. It looks the same as the one in the video, and it comes with many new washers and some silicon grease. I may check the micro switch if it is accessible, before any dismantling.Zoomy, admit it, you just like fixing things. ?
Gor blimey mate. It's a fair cop gov.
Z,