DISTRIBUTOR CANNOT BE TRUSTED...
Hi folks!
This is my first forum post and hopefully and interesting topic. I am looking for some advice on where to start!
Background:
  1. 4th floor apartment tear-out in the city of Baku, Azerbaijan in a very old Soviet-era building block with unknown amounts of modifications.
  • 4 wire system (3-phase and neutral) entering and distributed throughout the building (no armoured cable / no separate earth).
  • No enforced local regulations as the general wiring in the city is a free-for-all (I am told it should be to PUE 6 standard). I could share many examples but this is not the aim of this post!
  • No building plans available from the council / no wiring / single-line diagrams available for the building or from the distributor.
  • No option available for a reliable survey - Partly being that most of the local electricians think that an earth core is a waste of money!
  • Basically the local distributor cannot be relied upon as can be seen by the photo example of the electrical panel closest to the apartment from the local government electrical company...
  • I am an electrical engineer wanting to get my hands dirty with my own project compliant to the BS 7671 wiring regs. I will design the domestic electrical installation and will have it verified by an (UK) electrician / expat before proceeding and sourcing materials.
Aim:
  1. Brand new domestic apartment electrical installation to BS 7671 18th Edition in which is in my control (full rewire, new consumer unit etc.). BS exceed the local regulations.
  • Keep politics / what-should-be for the incoming panel out of the discussion, it is what it is and there is not much I can do except wait decades for regulations and enforcements to catch up!
  • Provide the safest solution to protect my family without running away from the building / country.
Closest Panel to my Apartment:
  • Ok lets cut to the chase - this may just be the worst panel that you have ever seen however I cannot modify it as it is owned by the local government electrical company. It gets no points for compliance to any regulation (maybe 1 for being metal only!). I unfortunately has to live with this monstrosity until the building is knocked down in the future (and this is one of the newer / better panels in the building believe it or not…1 of 3 panels up to the apartment).
34853545ae5c04645e1bb134ec9267e3-img_1749.pdf
Queries:
  1. Can I assume that the incoming supply is a TN-C-S (and I know this is the distributors responsibility…) i.e. connect the MET and neutral together before the consumer panel? I know we should never assume so what is the best way to test? I am trying to source a Megger. My concern is that this could bypass some protection elsewhere in the building although it appears to have only overcurrent protection (fuses).
  • Should I have a dedicated earth run from the incoming of the building (from the neutral bar) up to the apartment consumer unit instead? My concern is that there my be a potential difference between the neutral and the earth at the apartment which could require 2P RCBOs throughout. Yes there should not be a potential difference however there is a lot of twisted wiring (junction boxes are a luxury…) and poor looking connections as well as all the apartment neutrals connected together in the block.
  • A third option would be to have an earth pit installed in the car park and run the dedicated earth to the MET in the apartment although 2P RCBOs may still be required.
Any assistance is greatly appreciated including verification / testing methods before I dive into the design of the consumer unit. Thank you in advance,
Chris
  • I'm glad to see you are wearing gloves ? I hope there is someone with you in case you slip with all that exposed live in the box given the complete lack of any protection from the installation itself - I presume the camera operator is briefed on 1st aid ?
    I also see you have slipped into the local practice of stuffing the wire ends into the socket to test the lamp. This is scarily like the roughest bits of ost Berlin just after the wall came down, the difference is that in the last 30 odd years that stuff has all been demolished or modernised. (and there red was the earth and black live, usually, but not always.)
    Please don't be upset if it seems  I'm teasing you a little bit but I have a serious message - I hope we both know that in the UK  the H & S folk would be having kittens, and this really is not the sort of thing to be undertaken alone or anything other than wide awake and on a good footing in dry shoes.  I might wear also a long sleeved cotton shirt in your place. Consider that if something does go snackle pop in your hand and showers you with hot metal it may be the difference between needing a new shirt and needing a skin graft to your wrist and forearm.  It only needs something to fall onto the incomer terminals...  Even with skeleton substations in the UK, the DNOs now like to see big rubberised sheets draped over the live bits when folk have to work near them on anything else to reduce the risk of things falling into the works.
    Now to the results.
    Nice to see that some things are earthed, even if the gas main is not really what you want as the only reliable electrode (!!), this result also shows that your substation has an earth as well, which in the circumstances is a good thing to have verified. Normally it goes without saying, but maybe not here.
    The impedances to the building re-bar are more than a bit  underwhelming really, so that is clearly not going to serve as a main electrode.
    I guess the next one to think about is your water pump - is the incoming service pipe metal ?
    Edit sorry, did not answer the original question.
    To a small electrode I'd  consider 6mm or 4mm as a minimum - as noted below the resistance of the soil dominates, so the cable size is really set by the mechanics of not getting damaged by rats or the gardener, and not being so big as to look  attractive to thieves. To things that may have an NE bond elsewhere like the water pipes,  for your 32A supply, there is little point in anything more than 10 or 16mm2. Your whole intent is to have double pole breaking RCD cover, so a large enough N-E  diverted current to damage the cable is unlikely even in fault from your side.
    You cannot sensibly protect against a fault current coming up the gas pipe and going down the water that is not from your installation, do not try to, just position the bonding for those paths so that if it gets hot it does no damage, and it is likely to be spotted.
    I'm well aware that this is not matching the guidance for the UK, by a large margin, but what we need here is safety, not blindly following inappropriate rules
    AJJewsbury:
    How big is the N into the building? - no need to go larger than that I guess. In the UK we'd apply table 54.8 to the size of the supply N (e.g. 10mm² bonding for up to a 35mm² supply N, 16mm² for up to 50mm² etc up to 50mm² for over 150mm²) - so that would be my minimum (I'm presuming the main services aren't bonded where the enter the overall building) - so maybe somewhere between the two depending how the numbers worked out.
    The cable lugs on the cores for the incoming cable to the building have 185 mm² stamped on them and the diameter of the 4c cable / individual cores appear to match that.
    Table 54.8 applies to PME / TN-C-S supplies. I do not want to assume that the incoming neutral is a PEN conductor so err on the side of caution and apply 544.1.1 - therefore Table 54.7 (in absence of loop impedance testing to calculate instead).
    There is no bonding anywhere in the building as there is no incoming earth from the distributor and no earth conductors anywhere inside the flats to any extraneous pipework.
    • It would appear that the neighbours lead drainage pipe exits the building and runs down the wall right behind my water pump (I learn something everyday from the photos so need to verify that!). Also just noticed that the water pump has no pressure regulator on it! It must have been connected to a level switch in the old water tank that has since been removed.
    • The gas main runs around the building outdoors T-ing off to meters / combi boilers either enclosed in PVC enclosures outdoors or located within stairwells.
    • The water pipes are separate as there is a pump per flat however some of the metal pipework is in contact with or fixed to other structural metal work.
    All metallic pipework therefore comes out of the ground outdoors, with no bonding between them or anywhere throughout the building. The pipework exits the ground within the same area (bar the gas main which comes up around 20 metres away) which is a carpark surrounded by the building (square shaped).
    AJJewsbury:
    The problem is really just bonding to extraneous-conductive-parts that have a low impedance back to the source - which it looks like the gas pipes for one have. Things simply stuck in the soil - such as a TT earth electrode will have a resistance (due to the soil around it) of many Ohms - which will naturally limit the current to something relatively modest. So some care with the placement on bonds might reduce the costs a bit.
    Agreed, I have been going round in circles with this (at least I now know why CNE cables are not distributed within a block of flats, to avoid neutral diversion currents through extraneous pipework on a disconnected neutral within the block). I propose to bond the metallic pipework at ground level and bond the gas and lead drainage pipes together in the stairwell where they enter the building (see my updated PDF drawing below Rev03). This bonding (S/2 from Table 54.7 in this case half the incoming 185 mm² cable) would ensure equipotential bonding between the extraneous pipework, at least where the bond is located, and may improve disconnection times for a main cable to earth (pipe) fault. It would also mitigate you and I’s concerns for overloading the bonding within the flat (if this were to be the only bonding within the entire building) although I fully understand Mike’s point also. Some may argue that bonding at ground level is not required however I’m making no assumptions at this stage unless otherwise tested.
    AJJewsbury:
    That looks small for drainage - given that lead pipes (at least UK ones) usually have quite thick walls it looks like it would have a pretty small bore - much like a 1/2" water supply pipe.
    In the previous image 15, there are 2 lead pipes lagged together, the horizontal one is used for the shower drain and the other vertical one is used for the toilet. The outer diameter is around 2 inches. I could only get the clamp on the improper bend where it flattens out a little.
    mapj1:
    Please don't be upset if it seems  I'm teasing you a little bit but I have a serious message - ...
    Fully agree Mike, there is no excuse for lack of safety and that setup was as rough as it comes. It shall not be used again. The foreman was with me during testing and I am on the lookout for rubber matting to keep under that panel nearby the flat at all times. I cannot modify the distributor panels otherwise I would have terminal shrouds fitted. It is actually worse than we may think if the supply to the building can produce anything near the fault rating of the incoming fuses. There is no way that the main distribution panel could contain a 50 kA fault with its simple hinges and basic locks never mind the omitted gland plate at the bottom. Strictly speaking, something like this should really have an arc flash suit to access live as even when the disconnector is open, the incoming cable lugs are still bare. Not only that, the main panel is unearthed and could be lethal for the unfortunate cleaner mopping the ground floor nearby if a live conductor were in contact with the casing. These panels should be locked away from the public in separate rooms. At least the sub-distribution panel (middle) is the best of a bad situation whereby the panel earth is connected to the neutral which should clear a live conductor fault to the casing.
    mapj1:
    Correct, metal water pipe. It should be fun trying to change the pump out without a stopcock...
    I noticed 4 mm² was the minimum for TT systems in the OSG Table 4.4(iii) due to the fast RCD disconnection times I guess. Again erring on the side of caution I have used the TNS Table 4.4(i) 10 mm² which is oversized. I do plan to hide the main earth cable in some plastic conduit pipe to deter thieves and inquisitive locals wondering why there is an earth cable installed in the first place ...
    I have proposed a hybrid solution from both yours and Andy’s suggestions. Comments welcome. Thank you for your continued support :)
    CG Project Rev03.pdf
  • Your latest PDF looks quite sensible to me.
    Given the nature of the existing work, where no economy of cost or effort has been overlooked, the incomer may be 185 Aluminium in the wrong sort of lugs  of course, rather than copper, and that would still fit with the 250A incomer fuses, being good for ~ 350A.  It also makes the 400A fuses further up an example of wishful thinking...
    If so you could safely thin the bonds a bit, and base it on the 250A fuses.
    your proposed  95mm X bonds are probably over the top, but are quite short, which is good. For ease of fitting, and perhaps availability, they could be multiples of something more flexible to work with,  to achieve the same end. (like a few lengths of 10mm or 16mm in parallel.) Again not in UK regs, but a pragmatic hack.
    Is the water pump drawing from a well or is it boosting a significant street pressure ?
    If the latter I take your point about the lack of a street isolator. Ah, what we take for granted in the UK eh ?.
    The lamp test is OK for earth verification, but thinking further, I'd probably have used a live supply from a socket, via an extension lead rather than the bare board. I do realise there is a polarity uncertainty with 2 pin sockets, but that is manageable by trying both ways. And it was very useful to realise what is not earthed. (*)
    In the past when faced with toe curling areas of live metal I have been known to use plastic buckets, cut up flat plastic chopping boards and empty yoghurt pots and all sorts of ad-hoc domestic items as insulation of opportunity. I do not know if you ever saw the UK TV program Blue Peter as a kid, but the same creative skills that teach you to make a model light house from a washing up bottle can be re-used (un ?)professionally sometimes.
    We know in a well ordered world, you should not have to do so, but when you are not in a well ordered world the rules change a  bit  ?
    *You could even have 2 lamps in series and the test probe to the centre - if both come on dim the probe has no earth, one bright one dim good earth and a free polarity indicator  throw in (and half the potential shock voltage.)