This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

S.W.A. Cables in Parallel.

I have installed two 3 core 6.0mm2 S.W.A. cables in parallel for ease of installation, fused at 60 Amps.  The run is about 20 metres. They are single phase connected. I use Brown as L, Black tagged blue as N and grey oversleeved green and yellow as C.P.C. in each cable.


I have bonded the armour at each end and it is earthed at the origin of the circuit.


I have a niggling feeling that I have missed something. Is the above o.k?


Z.
Parents
  • alanblaby:


    Twin 6mm 3 cores?

    It would be far easier to run one 2 core 10mm, or even 1 x 2 core 6mm if clipped direct.

    This is basic stuff.


    Some wholesalers do not stock two core S.W.A. where 3 core is more popular. The 3 core was sold at the 2 core price.


    Would you run a 2 core 6.0mm2 S.W.A protected by a 60 Amp fuse?


    Z.


     


Reply
  • alanblaby:


    Twin 6mm 3 cores?

    It would be far easier to run one 2 core 10mm, or even 1 x 2 core 6mm if clipped direct.

    This is basic stuff.


    Some wholesalers do not stock two core S.W.A. where 3 core is more popular. The 3 core was sold at the 2 core price.


    Would you run a 2 core 6.0mm2 S.W.A protected by a 60 Amp fuse?


    Z.


     


Children
No Data