S.W.A. Cables in Parallel.
I have installed two 3 core 6.0mm2 S.W.A. cables in parallel for ease of installation, fused at 60 Amps.  The run is about 20 metres. They are single phase connected. I use Brown as L, Black tagged blue as N and grey oversleeved green and yellow as C.P.C. in each cable.
I have bonded the armour at each end and it is earthed at the origin of the circuit.
I have a niggling feeling that I have missed something. Is the above o.k?
  • Grey is usually used as neutral, and black as CPC.
    Twin 6mm 3 cores?
    It would be far easier to run one 2 core 10mm, or even 1 x 2 core 6mm if clipped direct.
    This is basic stuff.
  • alanblaby:
    Why?
    514.3.2
  • alanblaby:
    Twin 6mm 3 cores?
    Some wholesalers do not stock two core S.W.A. where 3 core is more popular. The 3 core was sold at the 2 core price.
    Would you run a 2 core 6.0mm2 S.W.A protected by a 60 Amp fuse?
  • The only problem with cables in parallel is what happens if the current share is unequal - actually a reasonable length helps here, on a short length the details of termination can be significant. So long as both armours, or more accurately any one would operate  the ADS if either cable was spiked, then it is fine. I'd be inclined to perhaps tie the ends together in some way, so they form a pair at the terminals, but that is only so it does not confuse any future person looking at it.
    Actually with 6mm and 60A you can have it quite a long way out of balance before it matters - it is a similar problem to the current share on the ring final, and we do not normally fuse the individual limbs there.
  • alanblaby:
    Twin 6mm 3 cores?
    Why?
    Yes it is the usual Zoom,
    One theory is that it is to dissassociate Black from N but in my world if you thing Red Yellow Blue then think Brown Black Grey you`d probably decide for Grey (oversleeved Blue) to be N . In the old R Y B many would use Blue nonsleeved as N because "it is a N colour as in Flexes" but that was a bit nawty not to oversleeve.
    In the Br Bk Blu system Black is oft oversleeved Brown as say a switched L with Brown as the Perm L similar to what you`d have done in the R Y B system. (where you be tempted to use Y (oversleeved) as the cpc or in new money the Black as Alan has said
  • mapj1:
    The two cables are of exactly equal length and supply a consumer unit. 4D4A does not rate 6.0mm2 anywhere near to 60 Amps.
  • Don`t ask me about my 6 core alarm cabling colour coding method when hardwiring an intruder alarm system - I think a few might agree but many might not do
  • Zoomup:
    mapj1:
    I'll just stick with 514.3.2 and Table 51 ebee. It is easy to identify cable cores as:
    a, They are oversleeved by the correct colour sleeving, or tagged by numbers or indicated by coloured tape.
    b, They are identified by their connections at terminations by observation.
  • I wonder if the underground / tube MULTI SWA's installed worry their electricians who installed them, years' ago??
    I don't see an issue with your install. Colour coding is a matter of preference although I personally use black as the CPC as long as you have identified your conductors its fine.
    Sounds like you have kept both cables the same length, if I were to do this I would add cable tags on the outer sheath (brass with steel ties) stating that both conductors are part of the same supply.