S.W.A. Cables in Parallel.

I have installed two 3 core 6.0mm2 S.W.A. cables in parallel for ease of installation, fused at 60 Amps.  The run is about 20 metres. They are single phase connected. I use Brown as L, Black tagged blue as N and grey oversleeved green and yellow as C.P.C. in each cable.


I have bonded the armour at each end and it is earthed at the origin of the circuit.


I have a niggling feeling that I have missed something. Is the above o.k?


Z.
Parents
  • Former Community Member
    0 Former Community Member
    I don't see an issue with your install. Colour coding is a matter of preference although I personally use black as the CPC as long as you have identified your conductors its fine.

    Sounds like you have kept both cables the same length, if I were to do this I would add cable tags on the outer sheath (brass with steel ties) stating that both conductors are part of the same supply.
Reply
  • Former Community Member
    0 Former Community Member
    I don't see an issue with your install. Colour coding is a matter of preference although I personally use black as the CPC as long as you have identified your conductors its fine.

    Sounds like you have kept both cables the same length, if I were to do this I would add cable tags on the outer sheath (brass with steel ties) stating that both conductors are part of the same supply.