Exterior armoured cable

Former Community Member
Former Community Member
I need to run an outside armoured cable to a pond pump. I will install all the necessary protection devices. My question is can the cable be laid loose on the ground between trees or attached to the trees. I dont really want to dig a trench all the way over a 40metre run. Thanks
Parents
  • Lawrie:

    I need to run an outside armoured cable to a pond pump. I will install all the necessary protection devices. My question is can the cable be laid loose on the ground between trees or attached to the trees. I dont really want to dig a trench all the way over a 40metre run. Thanks


    All pond pumps will eventually leak water into their internals and trip off a protecting R.C.D. even if not in use but still connected. (N-E fault). A double pole switch is best to prevent this happening. This fault can in certain circumstances trip off other circuits in a house which can be a nuisance or cause loss if freezers run back. A dedicated circuit for the pond pump is best, being completely separate from other circuits and not being supplied via an R.C.D. that protects other circuits such as in a split load consumer unit. Connecting to a ring final circuit is not a good idea.


    An extra low Voltage pump run through a mains  isolating transformer removes the risk of nuisance tripping of a house R.C.D. and is safer than using a 240 Volt pump.

    Z.


Reply
  • Lawrie:

    I need to run an outside armoured cable to a pond pump. I will install all the necessary protection devices. My question is can the cable be laid loose on the ground between trees or attached to the trees. I dont really want to dig a trench all the way over a 40metre run. Thanks


    All pond pumps will eventually leak water into their internals and trip off a protecting R.C.D. even if not in use but still connected. (N-E fault). A double pole switch is best to prevent this happening. This fault can in certain circumstances trip off other circuits in a house which can be a nuisance or cause loss if freezers run back. A dedicated circuit for the pond pump is best, being completely separate from other circuits and not being supplied via an R.C.D. that protects other circuits such as in a split load consumer unit. Connecting to a ring final circuit is not a good idea.


    An extra low Voltage pump run through a mains  isolating transformer removes the risk of nuisance tripping of a house R.C.D. and is safer than using a 240 Volt pump.