AJJewsbury:
I wouldn't expect SPD to offer any protection from longer-term overvoltage situations like broken neutrals - they operate by creating a low impedance L-PE or L-N and would have to dissipate huge amounts of (heat) energy if the overvoltage lasted for more than a small fraction of a second. The best we can hope for is that the SPD fails safe and disconnects itself before it starts a fire.
As for other solutions there are plenty of voltage monitoring relays on the market that could be fitted (probably via a contactor) to disconnect the installation if the voltage went outside limits. (e.g.https://uk.rs-online.com/web/p/monitoring-relays/9143945/ )
- Andy.
Good morning Andy, how do we connect one of these to a single phase installation? Just use one phase terminal of the three available? Or are there single phase versions available?
Z.
AJJewsbury:
I wouldn't expect SPD to offer any protection from longer-term overvoltage situations like broken neutrals - they operate by creating a low impedance L-PE or L-N and would have to dissipate huge amounts of (heat) energy if the overvoltage lasted for more than a small fraction of a second. The best we can hope for is that the SPD fails safe and disconnects itself before it starts a fire.
As for other solutions there are plenty of voltage monitoring relays on the market that could be fitted (probably via a contactor) to disconnect the installation if the voltage went outside limits. (e.g.https://uk.rs-online.com/web/p/monitoring-relays/9143945/ )
- Andy.
Good morning Andy, how do we connect one of these to a single phase installation? Just use one phase terminal of the three available? Or are there single phase versions available?
Z.