mapj1:
I have fitted capacitors N-E after a 4 pole RCD, so that if the NE voltage rises, the RCD sees the N-E current and fires and breaks everything but the CPC.
Just interested on people's views as to whether this stacks up with Regulation 531.3.1.202 ?
531.3.1.202 It is not permissible to introduce an external connection for the purpose of intentionally creating a residual current to trip an RCD.
However, I am compelled to point out that I'm asking this question with the full knowledge that many appliances have a capacitor connected between N and PE - but we are talking about of orders of magnitude difference in capacitance (1-10 nF in appliances, vs perhaps 10-20 μF to trip a 30 mA RCD for an N-E voltage of 50 V)?
Just edited to note that this Regulation was introduced in BS 7671:2018, and therefore I'm not necessarily saying that Mike's application was non-compliant at the time.
mapj1:
I have fitted capacitors N-E after a 4 pole RCD, so that if the NE voltage rises, the RCD sees the N-E current and fires and breaks everything but the CPC.
Just interested on people's views as to whether this stacks up with Regulation 531.3.1.202 ?
531.3.1.202 It is not permissible to introduce an external connection for the purpose of intentionally creating a residual current to trip an RCD.
However, I am compelled to point out that I'm asking this question with the full knowledge that many appliances have a capacitor connected between N and PE - but we are talking about of orders of magnitude difference in capacitance (1-10 nF in appliances, vs perhaps 10-20 μF to trip a 30 mA RCD for an N-E voltage of 50 V)?
Just edited to note that this Regulation was introduced in BS 7671:2018, and therefore I'm not necessarily saying that Mike's application was non-compliant at the time.