Loss of neutral

I have just been involved in a situation where temporary loss of neutral on a TNCS system caused thousands of pounds worth of damage. It seems this loss of neutral situation, either within or outside the installation, is occurring more frequently. SPDs are now commonly fitted but at DBS  and generally with a Up in the order of 860v, so giving no protection on loss of neutral in a three-phase and neutral system. Cost benefit analysis across the national spectrum might not support a compulsion but is it time designers should be raising the issue with clients and at least offering a solution. On the other hand, is there a packaged solution?
Parents
  • This occupancy sensor is typical of the damage inflicted. It is widespread with damage sustained to lots of electronic equipment. Of course, there is no hard evidence of loss of neutral and I suppose there are other possible causes.
Reply
  • This occupancy sensor is typical of the damage inflicted. It is widespread with damage sustained to lots of electronic equipment. Of course, there is no hard evidence of loss of neutral and I suppose there are other possible causes.