This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Loss of neutral

I have just been involved in a situation where temporary loss of neutral on a TNCS system caused thousands of pounds worth of damage. It seems this loss of neutral situation, either within or outside the installation, is occurring more frequently. SPDs are now commonly fitted but at DBS  and generally with a Up in the order of 860v, so giving no protection on loss of neutral in a three-phase and neutral system. Cost benefit analysis across the national spectrum might not support a compulsion but is it time designers should be raising the issue with clients and at least offering a solution. On the other hand, is there a packaged solution?
Parents
  • So, taking this discussion in a slightly different direction....


    What would be the general consensus/opinion about using a 4 pole REC isolator to disconnect (for a single phase domestic installation) the phase, neutral & also disconnect the water & gas bonds away from the network earth/neutral conductor? I'm thinking perhaps use two of two of the poles to switch two 25mm^2 conductors connecting the MET to the network earth/neutral to give some redundancy against a failed switch contact.


    Over to the floor....
Reply
  • So, taking this discussion in a slightly different direction....


    What would be the general consensus/opinion about using a 4 pole REC isolator to disconnect (for a single phase domestic installation) the phase, neutral & also disconnect the water & gas bonds away from the network earth/neutral conductor? I'm thinking perhaps use two of two of the poles to switch two 25mm^2 conductors connecting the MET to the network earth/neutral to give some redundancy against a failed switch contact.


    Over to the floor....
Children
No Data