Physics going on in a transformer
I’m trying to get a better understanding of the physics going on in a UK site transformer, those that reduce the UK mains voltage to 110V.
I’m fully aware of the basic operating principles of a transformer and the basic Power in equals V*I . Power out is the same as power in and induced voltage is given by Faradays law dependent upon the number of turns, and changing magnetic flux with time. With these we can work back from a load to determine the current draw from the secondary side of a transformer.
What I would like clarified is, depending upon the varying load on the secondary side, what at different loads is happening to the magnetic field strength in the core and the power in the primary side.
For example when I have a 1800W tool connected to my 3.3Kva 110V transformer and the power is on in the primary side but the load tool is not switched on. Obviously there is current flowing in the primary coil since there are no switches on these transformers apart from the socket switch. This will create a magnetic field which will induce an emf on the secondary windings.
If there is no load on the secondary side, is the magnetic field strength in the core and the power in the primary at its maximum even with no load on the secondary?
Or is primary input current much lower in comparison to what it could be if the transformer secondary is loaded to its maximum current output? Does putting a load on the secondary cause a feedback through the magnetic field resulting in the current increasing in the primary, hence increasing the magnetic field?
  • Hi Dave
    What i was told is that the magnetic field does stop.  When it restarts is when problems occur with circuit breakers as a peak current could add to the peak stopped position.
  • Yes Jon, but that suggests that the core was permanently magnetised. This is not the case with silicon steel used for transformers, the magnetic field is much too small to cause permanent magnetisation. The cause of the high peak current, as I said above, is that establishing a large field very quickly takes a very high current. Mike said that the highest rate of change of the magnetic field is at voltage zero crossings, but it is much higher still when directly connected to a high voltage, like the peak of a mains cycle, essentially instantly. Materials that remain magnetised are called hard magnetic materials, such as that used for permanent magnets, because they do not easily lose the magnetism, whereas soft ones (like silicon steel) do. It usually takes significant heat or physical deformation to demagnetise a hard material. Alloys such as AlNiCo, an aluminium-Nickel-Cobalt mixture make strong magnets, and some Rare Earth metals make the strongest ones, as used in modern permanent magnet motors. These would suffer demagnetisation very quickly in a motor where multiple magnetic fields interact, unless very hard magnetically.
    Another point which I didn't make is that transformers of some size make increased noise as the load gets larger, a loud hum. This is because the magnetic field is making mechanical changes to the core, and it does this even if the laminations are tightly clamped. One rarely sees this in magnetism sections of textbooks, there are physical changes in the atomic crystal structure caused by the magnetic field. I have been looking at a number of advanced physics books to quantify the size of the change, but it seems it is not mentioned. Logically though something physical must be happening to make a noise. Perhaps these writers had never been close to a large transformer, certainly, small ones cannot be heard easily. You may like to look here Wikipedia Ref.
  • Indeed- magnetics is badly explained in many books, and so it is often badly taught as well. And then folk confuse eddy currents from flux lines, and resistive heating with magnetic losses, when really they are orthogonal.
    The B field in the core is a bit like the voltage on the mains - more or less the same amplitude independent of load. The current drawn from the supply at that constant voltage needed to generate that B field however, does depend directly on the amount of current in the secondary.
    M.
  • davezawadi (David Stone):
    Another point which I didn't make is that transformers of some size make increased noise as the load gets larger, a loud hum. This is because the magnetic field is making mechanical changes to the core ...
    Oh no, DZ, you have that all wrong.
    It may seem to be a loud hum, but if you are sensitive to magnetic fields, you are feeling them direct.