Earthing of Neutral in Substation or MCB at LV Panel ? or both ?

Former Community Member
Former Community Member
Hello everyone! 


Im having some doubts regarding where I should ground the Neutral and why ?


This is a new installation which is in an industry that will have its own substation 15/0.4Kv with a transformer of 1250KVA 15/0.4KV DY.


This substation will only feed the MainCircuitBreaker of the plant which is located 80meters away from the substation, there will be no other consumers from this substation/transformer.


The cables are already buried. They will be 6 cables per phase alluminum 240mm2 and 4 other cables 240mm2 alluminum also that could be used for neutral or PE or PEN depending... 


Should I ground the neutral the the transformer ? at the income of the LV MCB ? at both sides ? run only a PEN from substation or run Neutral and PE separate ?


These are the possible options i was considering.. and was hoping some of you guys give your opinions. 


Remember the distance between the TX and LV main panel is 80m
5fdf97a7ed1bff695edece754561095b-huge-whatsapp-image-2021-04-08-at-16.16.32.jpg

In the picture the PEN in option 1 and earth in option 2 is grounded at both sides (transofmer and LV mainboard) 


The other options would be as 1) and 2) but grounding only at one of those sides... (those would be pure TNS or TNCS)


Whats your opinions ?!


Thanks in advance!!


Parents
  • Former Community Member
    0 Former Community Member
    Hi Mapj ! 


    1) This is not in UK but I have found this forum very helpfull and people with lot of knowleadge that might help me !

    2) In the substation there is the earthing grid below the substation. I dont know what you mean by hot or cold.. 


    The substation is 80 meters away from the main circuit breaker and might me like 180 meter from the las circuit breaker.


    The contractor suggested me to ground the neutral only at the main circuit breaker, and not at both sides.. 


    Also to tie the earth grid of the substation to the LV earth where the neutral is going to be grounded.. (80 meters away one from the other)


    They will be tied with a 240mm2 Al cable.


    Whats your opinion about this ?
Reply
  • Former Community Member
    0 Former Community Member
    Hi Mapj ! 


    1) This is not in UK but I have found this forum very helpfull and people with lot of knowleadge that might help me !

    2) In the substation there is the earthing grid below the substation. I dont know what you mean by hot or cold.. 


    The substation is 80 meters away from the main circuit breaker and might me like 180 meter from the las circuit breaker.


    The contractor suggested me to ground the neutral only at the main circuit breaker, and not at both sides.. 


    Also to tie the earth grid of the substation to the LV earth where the neutral is going to be grounded.. (80 meters away one from the other)


    They will be tied with a 240mm2 Al cable.


    Whats your opinion about this ?