Reactance and impedance of 300 mm2 Aluminium 4-core cable

Former Community Member
Former Community Member
I am doing 6.3.4 example in the IET Electrical installation design guide: calculations for electricians and designers. in part 2: three-phase to earth fault current at C, it says a 100m of 300 mm2 cable aluminium SWA thermosetting (Table F7A). but the table does not have x value, only r value. where and how to find these values to help in calculating the prospective fault current ?
Parents
  • Former Community Member
    0 Former Community Member
    I found it. I have the 4th edition which doesn't have the x and r values for aluminum. Here is a snap shot of the 2nd edition. I was really lost for a whole day.