Sparkingchip:
So long as the socket has shutters it complies with BS7671 doesn't it?
Compliant or not?
https://www.sparkswarehouse.com/products/emschsw-schuko-socket-unswitched-white-50-x-50
Sparkingchip:
Not quite that simple.
Regulation 511.1 applies. If the socket-outlet is shuttered, and complies with a British or Harmonized standard, (that is, HD nnnnn[-xx[-yy]] or EN nnnnn[-xx[-yy]]) then all is well. Otherwise, the 2nd para of Reg 511.1 requires the designer or specifier to confirm "not a lesser degree of safety" and Reg 511.2 applies and design documentation needs to be appended to the documentation shown in Part 6.
Legrand do shuttered versions of NFC 15-100 compliant socket-outlets (to NFC C 61-314), but because NFC C 61-314 is neither an HD nor an EN, you'd still need the confirmation paperwork conforming "not a lesser degree of safety".
gkenyon:
I suspect that the opinion may depend upon who is giving it. Would the French really admit that their sockets are less safe than ours?