Sparkingchip:
So long as the socket has shutters it complies with BS7671 doesn't it?
Not quite that simple.
Regulation 511.1 applies. If the socket-outlet is shuttered, and complies with a British or Harmonized standard, (that is, HD nnnnn[-xx[-yy]] or EN nnnnn[-xx[-yy]]) then all is well. Otherwise, the 2nd para of Reg 511.1 requires the designer or specifier to confirm "not a lesser degree of safety" and Reg 511.2 applies and design documentation needs to be appended to the documentation shown in Part 6.
Legrand do shuttered versions of NFC 15-100 compliant socket-outlets (to NFC C 61-314), but because NFC C 61-314 is neither an HD nor an EN, you'd still need the confirmation paperwork conforming "not a lesser degree of safety".
Sparkingchip:
So long as the socket has shutters it complies with BS7671 doesn't it?
Not quite that simple.
Regulation 511.1 applies. If the socket-outlet is shuttered, and complies with a British or Harmonized standard, (that is, HD nnnnn[-xx[-yy]] or EN nnnnn[-xx[-yy]]) then all is well. Otherwise, the 2nd para of Reg 511.1 requires the designer or specifier to confirm "not a lesser degree of safety" and Reg 511.2 applies and design documentation needs to be appended to the documentation shown in Part 6.
Legrand do shuttered versions of NFC 15-100 compliant socket-outlets (to NFC C 61-314), but because NFC C 61-314 is neither an HD nor an EN, you'd still need the confirmation paperwork conforming "not a lesser degree of safety".
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site