ebee:
PS in my opening statement second to last line my ref to a fig 8 might be misleading. I was refering to the r1 r2 crossover test to give R1 + R2 figure rather than the Fig 8 bridged ring situation which it is designed to find (amongst other things).
Makes me think that one of our more knowlegable members should sketch, rings, fig 8s, crab claws, lollipops, 3 & 4 leaf clovers, trees etc etc.
Could make a small book in its own right ?
Do any of us make a habit of doing the crossover test to see if we`ve absent mindedly done a fig 8 or do we just do the test on an existing circuit by virtue of thinking "I would never do anything so daft!" ?
When wiring a ring final we know how many cables we have installed. A "pure" ring has two 2.5mm2 T&Es at each socket or wiring accessory. If spurs are added then we may have three 2.5mm2 cables at a socket or accessory, but this makes terminating a bit more difficult. All those cables in one box. I have never wired a ring as a figure of eight either deliberately or accidently. I am quite happy with just an end to end resistance test for rings.
The worst thing that I have found generally is two rings crossed over at a consumer unit. Ring A Leg L1 to M.C.B. 1, but Ring A Leg L2 to M.C.B. 2 etc. So two M.C.B. have to be turned off to deaden the one ring. This is mainly seen with hot wire fuses.
Z.
That is assuming, of course, that T&E is used, but I don't quite see why you would install a ring with singles - better to have radial
I have personally installed rings with singles rather than T&E cables , two examples come to mind. The first was in a small machine workshop where steel trunking and metalclad sockets were installed around the walls. The bulk of T&E cable would soon clutter up the limited capacity of the trunking especially if the trunking contained other circuit cables as well.
The second example was an office where plastic dado trunking was installed, again using singles. The capacity was limited as it was three compartment dado trunking.
Z.
ebee:
I know it`s many years ago that I queried the age old saying that was taught in college etc as to the r1 & r2 cross connection to form a double loop and the statement was made that this gave the exactly the R1 + R2 reading of the whole ring when taken from any point on the ring.
The correct statement, is that the test between L and PE at any point on the cross-connected ring (r1+r2)/4 equals the maximum reading if a standard (R1+R2) test were to be performed, that could be measured at the furthest point on the ring, if there were an accessory to measure it at, when the circuit is connected normally.
But that's a lot of words ...
(r1+r2)/4 is never actually (R1+R2) at any other point in the ring when connected in normal use, because, as you move closer to the CU around the ring, either way from the furthest point, you end up with (R1+R2) dropping from its maximum of (r1+r2)/4 at the [notional] furthest point, to somewhere approaching zero when you get to the CU itself.
ebee:
More of a thought exercise really because we wouldn`t normally be working with rings and spurs approaching safe limits in reality anyway.
Well ...
When you have to pop down to the wholesaler's to get another reel of 2.5 mm² ...
It depends upon the size of the property. You could easily use up 20 m just getting to the first sockets on the second floor.
ebee:
I only realised that any radial connected to the ring (ie a spur) should be measured without the crossover or an error would creep in because it would be added to near ring midpoint reading
Ahhh, now I understand what you're getting at.
So, in a ring with spurs, the correct statements for verification should be correctly stated (ignoring measurement inaccuracies and dirty contacts of switches and socket-outlets etc.) as:
(a) At any point on the ring, (R1+R2) ≤ (r1+r2)/4; and
(b) For any spur off the ring, (R1+R2) ≤ (R1spur+R2spur)+(r1+r2)/4
... and if (b) written as a formula or equation (R1+R2)=(R1spur+R2spur)+(r1+r2)/4, this is often an over-estimate unless the spur is close to the mid-point of the ring.