Earth rod used in pme installation.

Came across an earth rod in the concrete floor of a rural garage.The Ra was 115 ohms.

Just wondering how effective in loss of neutral this would be.Most pipework was plastic,

so no mpb.Thanks for any opinions.

                                   Regards,Hz
Parents
  • If the installation draws 1A then you'd have 115V between the top of the rod and true earth (some distance away) - so "not much" I'd say.

       - Andy.
Reply
  • If the installation draws 1A then you'd have 115V between the top of the rod and true earth (some distance away) - so "not much" I'd say.