Came across an earth rod in the concrete floor of a rural garage.The Ra was 115 ohms.
Just wondering how effective in loss of neutral this would be.Most pipework was plastic,
so no mpb.Thanks for any opinions.
                                   Regards,Hz
  • If the installation draws 1A then you'd have 115V between the top of the rod and true earth (some distance away) - so "not much" I'd say.
  • seconded - perhaps if it lit low wattage warning light between it and neutral, or if there is an RF reason for grounding.
    Perfeclty ok for tripping an RCD on a TT island of course, but utterly defeated if you connect the PEN derived TNCs earth to it.
    As a carrier of significant fault currents you are not doing much better than you would with a rod in a flowerpot on the windowsill....