Does anyone have a table of the ccc and VD of aluminium core T&E cable, please?
Thanks
F
broadgage:
I appreciate that this is not actually answering the question, but are you certain that the conductors are aluminium ?
Tinned copper is is often mistaken for aluminium.
fair point. It's not my job actually.
Someone has asked elsewhere, with a picture of the ends of the cores, which certainly looks like alu all the way through.
No, but if you look at 543 you will see that the value of k of a copper conductor is about 2/3 that of aluminium, so I think that you could use the tables for a copper conductor of 2/3 the value of the CSA of the aluminium one.