Earth Bonding Gas & Water Pipes

Assuming the copper water pipe (above the stop-cock at end of MDPE pipe) is close to the gas pipe, is it acceptable/permissible for the earth bonding conductor to be a single 10 mm² green/yellow from the consumer unit to go to say the water 351 earth clamp, looped around the screw and then to the gas 351?  This without cutting the cable, so that it is one continuous length. Or if not looped around the crew, for a bare section to be opened up 3 strands and 4 strands and the screw fitted between?
Thanks.
Clive

Parents
  • Former Community Member
    0 Former Community Member
    Chris

    Whichever way you do it, there is a tendency for the strands to be flattened between the washer and the clamp.

    Some brands don't have a separate washer, just the rigid screw head with a "built in" washer as one integral rigid item

    If you poke the screw through, one side may be a little flatter than the other, but that's why there is a washer rather than just a screw head - it is able to slope a little whilst making contact.

    As above

    If you loop round a full 360°, you have 7 strands under most of the washer, but 14 where they cross over, so that must be worse.

    Perhaps I should have said only a 180 degree loop in case someone took it to mean 360 degrees!

    By my reckoning, you only need to go round 180°, which forms an omega shape.

    Fully agree as was my inference

    I think quicker and easier to form a loop than poking a screwdriver through the middle.

    And less risky to the paws!

    The reason for not cutting the cable is supposed to be that if the first termination is removed, the second one remains intact.

    As per the various guides, including the old RECs books for contractors on PME. and the late Geoffrey Stokes' book 12.3.1 along with GN8


    Plus of course the alleged unwillingness for manufacturers of the BS951 clamps to confirm the 3 + 4 etc combinations. Perhaps you'll have more luck Chris!


    Regards


    BOD
Reply
  • Former Community Member
    0 Former Community Member
    Chris

    Whichever way you do it, there is a tendency for the strands to be flattened between the washer and the clamp.

    Some brands don't have a separate washer, just the rigid screw head with a "built in" washer as one integral rigid item

    If you poke the screw through, one side may be a little flatter than the other, but that's why there is a washer rather than just a screw head - it is able to slope a little whilst making contact.

    As above

    If you loop round a full 360°, you have 7 strands under most of the washer, but 14 where they cross over, so that must be worse.

    Perhaps I should have said only a 180 degree loop in case someone took it to mean 360 degrees!

    By my reckoning, you only need to go round 180°, which forms an omega shape.

    Fully agree as was my inference

    I think quicker and easier to form a loop than poking a screwdriver through the middle.

    And less risky to the paws!

    The reason for not cutting the cable is supposed to be that if the first termination is removed, the second one remains intact.

    As per the various guides, including the old RECs books for contractors on PME. and the late Geoffrey Stokes' book 12.3.1 along with GN8


    Plus of course the alleged unwillingness for manufacturers of the BS951 clamps to confirm the 3 + 4 etc combinations. Perhaps you'll have more luck Chris!


    Regards


    BOD