This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Earth Bonding Gas & Water Pipes

Assuming the copper water pipe (above the stop-cock at end of MDPE pipe) is close to the gas pipe, is it acceptable/permissible for the earth bonding conductor to be a single 10 mm² green/yellow from the consumer unit to go to say the water 351 earth clamp, looped around the screw and then to the gas 351?  This without cutting the cable, so that it is one continuous length. Or if not looped around the crew, for a bare section to be opened up 3 strands and 4 strands and the screw fitted between?
Thanks.
Clive

Parents


  • Whatever convoluted replies are given, bonding a water pipe that is not an extraneous-conductive-part is not required and should not be done.



Reply


  • Whatever convoluted replies are given, bonding a water pipe that is not an extraneous-conductive-part is not required and should not be done.



Children
No Data