Earth Bonding Gas & Water Pipes

Assuming the copper water pipe (above the stop-cock at end of MDPE pipe) is close to the gas pipe, is it acceptable/permissible for the earth bonding conductor to be a single 10 mm² green/yellow from the consumer unit to go to say the water 351 earth clamp, looped around the screw and then to the gas 351?  This without cutting the cable, so that it is one continuous length. Or if not looped around the crew, for a bare section to be opened up 3 strands and 4 strands and the screw fitted between?
Thanks.
Clive

Parents
  • In defence of the Tenby clamp, surely there are plenty of terminals with a similar arrangement. Contactors spring to mind just now.


    So do you (thinking in general terms including say, 2.5 mm² singles):


    (1) put on a ferrule and, therefore, use only one side of the clamp; or

    (2) leave the strands naked and wrap around 180°?
Reply
  • In defence of the Tenby clamp, surely there are plenty of terminals with a similar arrangement. Contactors spring to mind just now.


    So do you (thinking in general terms including say, 2.5 mm² singles):


    (1) put on a ferrule and, therefore, use only one side of the clamp; or

    (2) leave the strands naked and wrap around 180°?