GrahamGibson:
Hi,
I have some bonding questions which I'm hoping that the experts on here can help with.
Example - TN-C-S installation with 25mm2 tails, 16mm2 main earthing conductor, 10mm2 main bonding conductors to incoming, buried metal water and gas pipes and 4mm2 supplementary bonding in the bathrooms.
Assuming the pipes have good conductivity to earth, am I correct in assuming that (1) during normal operating conditions, a portion of the 'return' current will flow via the bonding conductors & pipes (depending on the relative resistances of that path versus the main PEN conductor path) and (2) if the PEN conductor is damaged then all of the 'return' current will flow via the bonding conductors & pipes? If so, I'm wondering why 10mm2 bonding conductors are deemed to be sufficient, particularly in the latter case where a potentially large current is flowing and it is perhaps not obvious that a fault exists?
I also started thinking that, depending on the layout of pipework and how the supplementary bonding is done (e.g. multiple pipes coming off of the incoming water main that end up being supplementary bonded at some end point) that current could also be flowing in the supplementary bonding conductors in cases 1 and 2 above. Which then leads me to the question of why 4mm2 supplementary bonding conductors are deemed to be sufficient...
In my mind, the only way to be sure would be to measure the relative resistances of all of the various earth paths, but the regs quote the standard bonding conductor sizes without reference to this. Sorry if this is a silly question or if I'm missing something fundamental, but it's had me scratching my head recently. Any guidance gratefully received.
Regards,
Graham
I think that the magnitude of diverted neutral currents will be limited by the resistance to true earth of the conducting underground pipes. If the ground is dry or poorly conducting like sand, the currents may be low and cause no harm. If the roaming currents warm up and dry out the surrounding soil that will make it less conductive as well. I don't think that we have many day to day examples of diverted neutral currents causing fires or other disasters, but a year or so back we did read an account of 1.0mm2 lighting C.P.C.s having melted cables in a loft, if I remember correctly, due to diverted neutral currents. P.M.E. supplies have multiple earthing electrodes to reduce the likelihood of a neutral Voltage rise. I can see them installed at regular points at the base of poles that support overhead lines.
Z.
John Peckham:
My supply enters at the front of the house and the copper pipe enters at the rear. The 10mm bond runs under the 1st floor floor boards. I have inserted a plastic joint directly after the water stop valve and the 10mm bond clamp after the plastic joint. That way I will not have diverted neutral currents flowing in the bond and setting light to my house.
If I have understood correctly, haven't you just disconnected the 'bonding' conductor from the extraneous-conductive-part thus negating the conductor's true purpose and making its presence futile?