Bonding questions

Former Community Member
Former Community Member
Hi,


I have some bonding questions which I'm hoping that the experts on here can help with.


Example - TN-C-S installation with 25mm2 tails, 16mm2 main earthing conductor, 10mm2 main bonding conductors to incoming, buried metal water and gas pipes and 4mm2 supplementary bonding in the bathrooms.


Assuming the pipes have good conductivity to earth, am I correct in assuming that (1) during normal operating conditions, a portion of the 'return' current will flow via the bonding conductors & pipes (depending on the relative resistances of that path versus the main PEN conductor path) and (2) if the PEN conductor is damaged then all of the 'return' current will flow via the bonding conductors & pipes?  If so, I'm wondering why 10mm2 bonding conductors are deemed to be sufficient, particularly in the latter case where a potentially large current is flowing and it is perhaps not obvious that a fault exists?


I also started thinking that, depending on the layout of pipework and how the supplementary bonding is done (e.g. multiple pipes coming off of the incoming water main that end up being supplementary bonded at some end point) that current could also be flowing in the supplementary bonding conductors in cases 1 and 2 above.  Which then leads me to the question of why 4mm2 supplementary bonding conductors are deemed to be sufficient...


In my mind, the only way to be sure would be to measure the relative resistances of all of the various earth paths, but the regs quote the standard bonding conductor sizes without reference to this.  Sorry if this is a silly question or if I'm missing something fundamental, but it's had me scratching my head recently.  Any guidance gratefully received.


Regards,

Graham
Parents
  • In principle your concern is well founded, but it all hinges on what really is a 'good' connection to what I shall call the  terra-firma earth, not to be confused with the MET earth or the CPC earth.....


    This is an area that BS7671 does not handle very clearly, indeed it is fair to say that the best approach to earthing and bonding or not has rumbled on as being a bit contentious since the first edition of the regs in the 1880s, getting worse ~ 100 years later in the 1980s as PME and bonding mania co-incided, and has eased a bit with the RCD


    The problem for the PEN fault is there is no sensible totally  safe size, unless you go totally impractical and use the substation fuses as your guide, as the diverted current via your pipes and NE bond may be much larger than the rating of your service cable, in the case of a fault where your house now carries the neutral current of the rest of the street.

    However it is almost never that bad - there is not normally a case where only one properly has functioning main bonds and no-one else does, so the current,  which on a typical 3 phase supply is smaller than the phase currents anyway, is divided by many paths.


    That's not to say there are not odd things that happen ( like in this US video) but the cable sizes are a compromise as the alternative is  too unwieldy. 

    One could consider fuses in the earth path to protect the cables, but there are other very good reasons why we do not do this.


    At the same time the standards to not distinguish things that are really loosely earthed, like short lengths of pipe between say an oil tank and a boiler house, or planted 'street furniture'  where the resistance as an electrode cannot be less than several tens of ohms, and a really thin bit of wire would be more than adequate.

    Insulated joints (" I J "s to the gas people ) are a thing and slowly becoming more common, but can make other situations worse, as there may be different voltages on either side of that join.

    Mike



Reply
  • In principle your concern is well founded, but it all hinges on what really is a 'good' connection to what I shall call the  terra-firma earth, not to be confused with the MET earth or the CPC earth.....


    This is an area that BS7671 does not handle very clearly, indeed it is fair to say that the best approach to earthing and bonding or not has rumbled on as being a bit contentious since the first edition of the regs in the 1880s, getting worse ~ 100 years later in the 1980s as PME and bonding mania co-incided, and has eased a bit with the RCD


    The problem for the PEN fault is there is no sensible totally  safe size, unless you go totally impractical and use the substation fuses as your guide, as the diverted current via your pipes and NE bond may be much larger than the rating of your service cable, in the case of a fault where your house now carries the neutral current of the rest of the street.

    However it is almost never that bad - there is not normally a case where only one properly has functioning main bonds and no-one else does, so the current,  which on a typical 3 phase supply is smaller than the phase currents anyway, is divided by many paths.


    That's not to say there are not odd things that happen ( like in this US video) but the cable sizes are a compromise as the alternative is  too unwieldy. 

    One could consider fuses in the earth path to protect the cables, but there are other very good reasons why we do not do this.


    At the same time the standards to not distinguish things that are really loosely earthed, like short lengths of pipe between say an oil tank and a boiler house, or planted 'street furniture'  where the resistance as an electrode cannot be less than several tens of ohms, and a really thin bit of wire would be more than adequate.

    Insulated joints (" I J "s to the gas people ) are a thing and slowly becoming more common, but can make other situations worse, as there may be different voltages on either side of that join.