EICR - main earth and neutral

Former Community Member
Former Community Member
Hi was conducting a EICR on a consumer unit today removed the cover and Main earth cable was 8 x single strand insulated cables istead of expected single 25mm also earth was the same??? it is in an apartment and has been running fine for

at least 20 years, just want to know what to input for csa?? and should I note it in observations under C3 CODE???? ANY ADVISE WELCOME THANKS
Parents
  • If it looks a bit like this stuff. then as others have said,
    59d15a4653d6b028bdef62fe6ee9b319-original-splitcon.jpg


     It is split concentric cable - common for use by DNOs, not quite as good as SWA as there is not an overall earthed armour - half of the 'not really an armour' is neutral. but easy to work with and good for EMC. Can be buried, but needs to meet the same routing rules in walls like T and E to meet BS7671.

    CSA is normally stamped on the jacket, but if not, size from the live core, N has slightly more current handling capacity, being better cooled

    Mike
Reply
  • If it looks a bit like this stuff. then as others have said,
    59d15a4653d6b028bdef62fe6ee9b319-original-splitcon.jpg


     It is split concentric cable - common for use by DNOs, not quite as good as SWA as there is not an overall earthed armour - half of the 'not really an armour' is neutral. but easy to work with and good for EMC. Can be buried, but needs to meet the same routing rules in walls like T and E to meet BS7671.

    CSA is normally stamped on the jacket, but if not, size from the live core, N has slightly more current handling capacity, being better cooled

    Mike