EICR - main earth and neutral

Former Community Member
Former Community Member
Hi was conducting a EICR on a consumer unit today removed the cover and Main earth cable was 8 x single strand insulated cables istead of expected single 25mm also earth was the same??? it is in an apartment and has been running fine for

at least 20 years, just want to know what to input for csa?? and should I note it in observations under C3 CODE???? ANY ADVISE WELCOME THANKS
Parents
  • istead of expected single 25mm

    As it's an apartment, I wouldn't be at all surprised if it was fused down after the cut-out - and thus a smaller size could be expected (often 16mm² perhaps even 10mm² if the load was expected to be modest).


    Split-con often used to be used in place of SWA (as it's much easier to handle and terminate), but has a few disadvantages for modern requirements - firstly much of the "armour" is N rather than PE, so it's not suitable for avoiding 30mA RCD protection when concealed in a wall or similar - so basically treat it as if it were T&E rather than SWA. Also some care is needed with fault protection - since the plastic covering on the individual strands of the N mean that fault currents aren't necessarily shared between all of the strands if the fault occurs before the final terminal, unlike a normal stranded conductor, so you might want to think about  fault protection of conductors in parallel (e.g. appendix 10 of BS 7671).


       - Andy.
Reply
  • istead of expected single 25mm

    As it's an apartment, I wouldn't be at all surprised if it was fused down after the cut-out - and thus a smaller size could be expected (often 16mm² perhaps even 10mm² if the load was expected to be modest).


    Split-con often used to be used in place of SWA (as it's much easier to handle and terminate), but has a few disadvantages for modern requirements - firstly much of the "armour" is N rather than PE, so it's not suitable for avoiding 30mA RCD protection when concealed in a wall or similar - so basically treat it as if it were T&E rather than SWA. Also some care is needed with fault protection - since the plastic covering on the individual strands of the N mean that fault currents aren't necessarily shared between all of the strands if the fault occurs before the final terminal, unlike a normal stranded conductor, so you might want to think about  fault protection of conductors in parallel (e.g. appendix 10 of BS 7671).